If fuses of 250 mA, 500 mA, 1 A, 5 A and 10 A were available, which one would be the most suitable for protecting an amplifier rated at 240 V, 180 W?
Answer
Add a comment
Add a comment
Topic Tags
1 Answer
0
02/08/2021 11:49 am
P = VI
I = \(\frac{P}{V}\)
= \(\frac{180}{240}\)
= 0.75A
The fuse wire should be such that it is able to withstand only a little more current than 0.75A. So the fuse of 1A is the most suitable.
Add a comment
Add a comment
Forum Jump:
Related Topics
-
Explain the underlying principle and working of an electric generator by drawing a labelled diagram. What is the function of brushes?
4 years ago
-
When does an electric short-circuit occurs?
4 years ago
-
What is the function of an earth wire? Why is it necessary to earth metallic appliances?
4 years ago
-
State the rule to determine the direction of a (a) magnetic field produced around a straight conductor carrying current (b) force experienced by a current-carrying straight conductor placed in a magnetic field which is perpendicular to it, and
4 years ago
-
Two circular coils A and B are placed closed to each other. If the current in the coil A is changed, will some current be induced in the coil B? Give reason.
4 years ago
Topic Tags:
class 10 (8819)
,
lakhmir singh (3364)
,
magnetic effects (388)
,
electric current (477)
,
Forum Information
- 321 Forums
- 27.3 K Topics
- 53.8 K Posts
- 29 Online
- 12.4 K Members
Our newest member: Stripchat
Forum Icons:
Forum contains no unread posts
Forum contains unread posts
Topic Icons:
Not Replied
Replied
Active
Hot
Sticky
Unapproved
Solved
Private
Closed